If the generator breaker opened while at high load, You have 1 SECOND to respond before the steam turbine accelerates to emergency trip speed.
So If the generator lost sync (tripped), you should notice the turbine running near rated speed (not synch speed) or the speed settling back to rated once the govenor performed its function.
So if the question was "When the generator is tripped but the turbine is running near rated speed, what would you do?" to answer would require knowing what was the desired condition prior and the current expected condition. If it were "On Line". then determine the reason for the generator seperation, If that was knowm and no corrective action required, then re synching could be the answer. If the reason for breaker open was not known and expected correction would be needed, I would not keep a hot turbine running at no load. I would look a log to see when last over speed trip test was performed and if needed, take advantage of the tripped generator and perform OST then return the unit to turning gear while the generator problem is resolved.
Most over speed event (wrecks) start with the operators statement, "When the turbine was tripped, the generator was still in sync with load, so I..." Expaination (for most utility logic in the US), when the turbine is tripped, valves close and stop steam flow so generator load quickly reduces. once the reverse power relay times out, the generator breaker is open. IF one of the steam valves fails to close when the turbine is tripped, the generator will stay synched, producing the power from the steam flow through the failed valve.
unfortunately when this situation occurs, the wrong answer is trip the generator breaker, wrecking the unit. the correct answer depends upon station design. Do you have boiler block valves, if not how can you dump the boiler pressure QUICKLY and during this process keep a close eye on excitation to ensure the generator does NOT trip till steam flow is reduced to reverse power. Remember, overspeed trip is no longer operational since a steam valve is failed open so even with minimun load, the turbine will slowly accelerate and possibly wreck (for really low load breaker opening, the turbine could reack stall before damaging speed)