I worked on the turbine side, so I might not be correct in boiler control terminoligy,
having the CVs set at a less than 100% opening and sliding boiler pressure to control load was a practice I witnessed.
I discussed with several plants about choosing an exact "best valve position", ie close sequential CVs for a 4 valve unit, so #1 & #2 are open to point where #3 is just closed, and use that position to slide pressure for nightly reduced load operation