According to IEC60364, for TN-systems and protection against electrical shock:
413.1.3.3: It is said that Zs*Ia <= U0, i.e. system-impedancem multiplied by the minimum current that assures that the breaker is disconnected within a given time should be less than the nominal phase-voltage.
The time is given as a table, and for U0=230V (i.e. TN Ull=400V) the maximum time is 0,4 seconds.
So, if the minimum faultcurrent that occurs is quite large, and the system-impedance is kept quite low, you should be able to fulfill this requirement with a MCB, depending on it's caracteristics (B,C,D) and the calculations you do. The whole clue is to assure that the fault is limited and disconnected after a short time. You must assure that your MCB will disconnect in the electromagnetically (within the time) and not thermal area of its caracteristic curve. If the faultcurrent is too small to trip the breaker, then you've done something wring.
However; 413.1.3.4 says that the time requirement mainly goes for portable-,handheld equipment or equipment connected with a socket outlet........ As opposed to
413.1.3.5: For stationary equipment, i.e. mounted to the wall, and not supplied from outlets et.c., you can allow a time up to 5 seconds. Then the requirement is that the impedance in should not exceed 50V*Zs/U0, and there is to be connected an equipotential bonding concductor.
THEN 413.1.3.6: If the requirements from 413.1.3.3, 4 or 5 above cannot be fulfilled by using regular overcurrent protection (typically MCBs), one is supposed to use equipotential bonding concductor and/or RCD.
---
So the real requirement is made to the system impedance, and to get rid of the fault within a specified time. Sometimes, you need a RCD to obtain this in a TN-system.