ogbuehi
Electrical
- Aug 1, 2007
- 30
We have a contractor submitting a cable that he is requesting our approval on. The load is rated for 300A so he submitted submitted a 300mm^2 (1 run, all phases and neutral in one cable). The voltage is 380V. This cable is to be buried directly in earth and concrete-encased in a electrical duct when the cable runs under the roadway. The conductor is copper and insulation is XLPE PVC sheathed cable. The cable he submitted is multi-core (see attached PDF, page 18 on the document or page 19 by what Adobe says). The code we're using is NEC and I'm having a hard time in 310 trying to find what table applies to this cable. I thought maybe it could be considered triplexed cable but there are 4 current carrying conductors in the cable itself. I don't have access to the cable specifications I would need to do a manual calculation (dielectric loss temperature rise, dc resistance of conductor at temperature, effective thermal resistance between conductor and surronding ambient etc..). I was wondering if anybody had dealt with this type of cable in determining it's current carrying capabilities.