rockman7892
Electrical
- Apr 7, 2008
- 1,176
I am trouble shooting the attached circuit that keeps tripping both of the breakers in the circuit (coordinatin issue) from what appears to be a ground fault. Both circuit breakers keep tripping intermitently. The circuit shown is a 480V L-L single phase circuit. The load will sometimes run for hours before tripping only to be rest and then trip out right away. After waiting some time the breakers can be reset and the circuit continues to operate.
I put a power meter on the circuit to see what is going on when the breakers trip. During normal operation I see current on both legs of the circuit at about 170A. However right as breaker trips I see the one leg as indicated on the sketch jump up to about 700A or so. I thought this was weird that only one leg would go high and not the other so I suspected there may be a ground fault. I set up another zero sequence CT around both of the legs as shown and find that when the breaker trips the meter sees the 700A on the one leg as shown as well as the zero sequence CT. Zero sequence CT reads 0 during normal operatioin. Seeing this I am suspecting there is a ground fault on the primary of the circuit somewhere on the one phase as indicated? Do you agree?
We went through and meggered both the cables and the primary of the transformer as shown in the circuit and everything is clear. We cannot seem to find eveidence of a short anywhere.
My thought is that it has to be a ground fault on the primary of the circuit. If there is a ground fault or any other type of fault on the secondary of the circuit then this would only appear as an overload on the primary of the transformer correct? In other words I there was a ground fault in the secondary of the transformer wouldn't this appear as an overload on the priamry with current seen in both primary legs as opposed to just 1?
Do you agree that what I am seeing must be a ground fault on the primary of the transformer circuit?
The only thing I'm not sure about is the SCR. Could something be going on with this to see what I am seeing?
I put a power meter on the circuit to see what is going on when the breakers trip. During normal operation I see current on both legs of the circuit at about 170A. However right as breaker trips I see the one leg as indicated on the sketch jump up to about 700A or so. I thought this was weird that only one leg would go high and not the other so I suspected there may be a ground fault. I set up another zero sequence CT around both of the legs as shown and find that when the breaker trips the meter sees the 700A on the one leg as shown as well as the zero sequence CT. Zero sequence CT reads 0 during normal operatioin. Seeing this I am suspecting there is a ground fault on the primary of the circuit somewhere on the one phase as indicated? Do you agree?
We went through and meggered both the cables and the primary of the transformer as shown in the circuit and everything is clear. We cannot seem to find eveidence of a short anywhere.
My thought is that it has to be a ground fault on the primary of the circuit. If there is a ground fault or any other type of fault on the secondary of the circuit then this would only appear as an overload on the primary of the transformer correct? In other words I there was a ground fault in the secondary of the transformer wouldn't this appear as an overload on the priamry with current seen in both primary legs as opposed to just 1?
Do you agree that what I am seeing must be a ground fault on the primary of the transformer circuit?
The only thing I'm not sure about is the SCR. Could something be going on with this to see what I am seeing?