Trouble shooting a three phase delta 240v bank. 1

Status
Not open for further replies.

lines04

Electrical
Apr 18, 2010
6
On a three phase delta 240v bank consisting of 3 single phase transformers, I am getting a phase to phase voltage of 120v,120v,240v. The problem is a crossed primary supply with two phases at the same potential. Can anyone explain to me how this works. Thank you
 
Replies continue below

Recommended for you

Phase A - B, Phase A - C and Phase B - C should read 240 volts. Depending how the phases are wires Phase A to gnd 120
Phase B to gnd 120 and Phase C to gnd 208 volts. Your reading indicate one of the phase fuses is blown.
 
If one of the primary fuses were blown on the high side of the transformer, you would get a 210v, 210v, 0v phase to phase. The delta bank im refering to is a three-wire secondary. The question im asking is why would you get 120v 120v, 240v on the secondary side if the red and white phase were at the same potential. (two primary wires wrapped downline)
 
What do you believe would happen in a three phase 240 delta bank if a two of the primary phases were at the same potential?
 
In my situation three single phase transformers are connected or bridged to get the voltages. The diagram you have provided me with is a Delta wye with the delta being the primary side. The situation im dealing with has a wye side and a delta secondary side
 