ThePunisher
Electrical
- Nov 7, 2009
- 384
Hi all,
I received a complaint from our client which indicates that the external trip relay used to energize the trip coil is having under-rated output contacts.
This relay is Phoenix Contact Part #PSR-SCP-24DC/ESP4/2X1/1X2, coil rating 24Vdc, output contacts rated at 110Vdc, 6A continuous/inrush rating, 42W (T=40ms)interrupting rating at inductive load, suitable for SIL 3 application.
The circuit breaker is Powell Vac-AR, 5kV, 3000A with trip and closing coils drawn current is 3.2A.
The circuit is generally wired so that this trip relay output NO contact is in series with the trip coil (in parallel with the protective/lockout relay contacts) and the trip relay NC contacts is wired in series with the circuit breaker closing coil as a closing interlock. This trip relay is operated on a non-fail safe and contacts only operate if the relay coil is energized. The comment is based on 42W at 110Vdc comparison with 3.2A trip/closing coil rating.
I disagree with the comment technically because the relay output contact wired to "close-In" or "make" to energize the trip coil which is rated at 3.2A. Since the output contact is rated at 6A, it should be ok. Furthermore,the trip or closing coil is de-energized by 51a and 52b simultaneously after the breaker operates.
Consequently, this also applies to the NC closing interlock contact on the closing coil circuit.
Do you agree with me? any thought otherwise?
I received a complaint from our client which indicates that the external trip relay used to energize the trip coil is having under-rated output contacts.
This relay is Phoenix Contact Part #PSR-SCP-24DC/ESP4/2X1/1X2, coil rating 24Vdc, output contacts rated at 110Vdc, 6A continuous/inrush rating, 42W (T=40ms)interrupting rating at inductive load, suitable for SIL 3 application.
The circuit breaker is Powell Vac-AR, 5kV, 3000A with trip and closing coils drawn current is 3.2A.
The circuit is generally wired so that this trip relay output NO contact is in series with the trip coil (in parallel with the protective/lockout relay contacts) and the trip relay NC contacts is wired in series with the circuit breaker closing coil as a closing interlock. This trip relay is operated on a non-fail safe and contacts only operate if the relay coil is energized. The comment is based on 42W at 110Vdc comparison with 3.2A trip/closing coil rating.
I disagree with the comment technically because the relay output contact wired to "close-In" or "make" to energize the trip coil which is rated at 3.2A. Since the output contact is rated at 6A, it should be ok. Furthermore,the trip or closing coil is de-energized by 51a and 52b simultaneously after the breaker operates.
Consequently, this also applies to the NC closing interlock contact on the closing coil circuit.
Do you agree with me? any thought otherwise?