Uquresh1
Electrical
- May 17, 2010
- 47
For Trip Coil monitor and Close coil monitor we use a Protection relay Input (high Impedance) wired in parallel to the Tripping relay output contacts, and in series with the Trip/close coil and the 52a/b status.
Has anyone ever had issues where the relay input (125VDC control voltage) would not pickup due to the voltage drop across the Trip/Close Coil? A vendor brought that up that they would like to set the relay Input to pickup for almost half of the full VDC, so around 65VDC, since they expect voltage to possibly drop to that value across the TCM/CCM Input.
I have never heard of a Trip or close coil creating such a big voltage drop that the Input only sees 50-60% of the full DC. Any help is appreciated.
Has anyone ever had issues where the relay input (125VDC control voltage) would not pickup due to the voltage drop across the Trip/Close Coil? A vendor brought that up that they would like to set the relay Input to pickup for almost half of the full VDC, so around 65VDC, since they expect voltage to possibly drop to that value across the TCM/CCM Input.
I have never heard of a Trip or close coil creating such a big voltage drop that the Input only sees 50-60% of the full DC. Any help is appreciated.