Thanks Skogs. Foolish and brave.
Yeah Dan, ain't it great!
Brian; You're right! Emitter. Yes I get it now.
Today I installed the unit back in the furnace and fired it up. Instantly it was obvious it wasn't running correctly. It makes a grating dental-drill sound due to nasty harmonics. I broke out the unidirectional test-lamp. Sure enough one/half channel was missing.
Running the test points showed all the channels running correctly on that side. So, I ran down the transistor cases. They all showed correct waveforms too. Right up until I touched the &](^#^#%%@$ case of one with the probe ground-ring, pffft! That half channel was also now gone.
So yes Brian that certainly does it!
Turned out Fry's carried that transistor. So in 45 minutes we were back up. I very, VERY, carefully probed the transistors after wrapping the ground ring in electrical tape. All channel fine. (Skogs that's the only confirmed time I did it!)
I switched to looking at the final output to the SCRs on the control board. Every gate was running with 1.4V pulses except one. It was 7V.
I powered down and unplugged all the outputs. Powered up and re-measured. Now all the channels were 7V. Bingo.
The trigger line was open at the snubber board somewhere. Where? Get this.. The terminal block was failed. The internal pin that connects the flat screw surface to the circuit board was sheared. Sometimes it would make and lately it wasn't very often. Turned out for that line on that snubber board there was another unused terminal that was paralleled to that same signal. Moving the control wire to that screw fixed the problem.
Next!
Thanks for all the help folks.
Keith Cress
kcress -