Hi.
I think our discussion is about different things.
Word "redundancy" make some misunderstanding.
I told about "redundancy" on HW level, that means:
Maintenance of one of xfr.
Power supply of plant in case of trip in one of xfr.( is reduce outage time in case of xfr. repair)
Flexibility in case of problem on one of BB (CB fault, SC on one of BB, etc.)., that mean possible fed MCC,etc on low level from energ. BB.
ATS as "simple" system, long delay ( several seconds), operated by UV situation. Not special MV transfer switch
and not high speed bus transfer switch.
Paralleling operation of two xf. for full redundancy is other story:
Protection coordination ( see post of Raghun).
Tap changer coordination ( master, follower, etc.).
Other level of current fault.
May be other primary swg.
I think is good for critical MCC's and switchboards, but not for grid connection to plant. Is not hospitals, FAB's.
Regards.
Slava