For lowside windings of ≤25kV, phasing voltmeter sets are routinely available for tests at the open lowside tie. Plan on making, recording and evaluating 15 voltage readings before closing the tie. PT secondary readings may also be used provided that PT connections have been shown to accurately reflect the two sets of ø-ø and ø-grd bus voltages.
Unmatched neutral-grounding resistors or dissimilar configurations need investigation. Be aware of incraaesed fault duties in the paralleled configuration.
Also, you might anticipate significant var circulation between the two units—potentially on the order of 1MVAR.