Most plants can be operated without 220 (or 240, whatever you want to call it). You will probably end up with a 45kVA 480 to 208Y/120V three-phase dry-type transformer mounted on a concrete pad on the floor. At 208V, a 30 kVA xf will serve a 100A main breaker, 45kVA will serve a 150A MB.
William