It all depends on the transformer winding configuration, the grounding arrangements, the importance of the transformer, how quickly it can be replaced or repaired if an internal fault occurs, and the degree of protection you want to apply. A 18.5MVA transformer is not an of-the-shelf item - in my opinion the more reliable protective schemes, the beter. Depending on the winding configuration, an additional REF-scheme incorporated into the diff-scheme (to obtain a combined REF/diff scheme) can easily be implemented, and it needs just a few extra items.
Finaly, as pointed out by several posters, the final decision depends on the client. Show him the advantages and disadvantages and let him makes the desicion.