Not really. That is the conductor temperature inside the insulation. The transformer manufacturers have thermal models of their transformers that allow a thermal probe in one location to "measure" the temperature in another location. From the description of your transformer, it is likely a small, dry-type, transformer without any thermal monitoring. Don't overload it, and don't expose it to an ambient temperature in excess of 40 deg C and you won't need to worry about the winding temperature rise.
Winding temperature becomes more of an issue with larger transformers, particularly those that use cooling systems to allow more capacity than the self cooled rating of the transformer.