Let remind ourselves the basics, since we went a bit off track and some suggestions are not correct:
(By the way fully agree with scottyUK and rbulsara)
The commonly held misconception about motor starting is that:
The start current of a motor is dependant of a motor driven load. (artym)
The fact is:
The start current of a motor is dependant on motor design, rotor speed and stator voltage from zero speed until full speed is reached.
The load will influence the time taken for the motor to reach full speed.
The current/speed curve of the motor is independent of all external influences other then stator voltage
When a motor is atationary, the motor current is limited by the effective series impedance of the rotor and stator.
At very low speeds, the dominant impedance is the rotor.
At high speeds, the stator impedance can become influential.
Therefore:
The rotor determines the starting characteristics of the motor while the stator has an influence on the full speed characteristics.
Motors, including large motors, are design for DOL full voltage starting(except most Slip Rings as they have external rotor resistance).
It is the allowable voltage drop on the plant/power system that may require other starting methods. Hence, limitation of power source must always be considered when applying motors, especially large motors, all up stream imedances must be known and starting volts drop calculated.
The motor in the question is small in kW and the original question was not re. volt drop but the transformer size; the question was correctly answered in the first replay by scottyUK.