A Pad Mount Transformer Y-yn Configuration, 34.5KV Ungrounded Wye Primary, 400/230V Solidly Grounded Wye Secondary.
When voltage at secondary side at no load was checked, the following were read: L1-L2=396V, L2-L3=398V, L3-L1=396V, L1-N=245V, L2-N=212V, L3-N=239V.
Since the wye primary neutral is not grounded, the 3rd harmonic current component of the transformer magnetizing current is restrained and it may have caused voltage distortion on the secondary L-N due to 3rd harmonic voltages at L-N. This is how I see it, but it would not harm me to consult further.
Another reason can be that the secondary neutral ground is not properly or effectively connected to ground.
Is there any other cause why Line to Neutral Voltage in the secondary side is unbalance?
I always been a fan of having both primary source and transformer primary neutrals grounded. Is it possible to have the Y-y transformer primary and secondary neutral grounded and leave the power source neutral ungrounded ( or a delta primary source)?
When voltage at secondary side at no load was checked, the following were read: L1-L2=396V, L2-L3=398V, L3-L1=396V, L1-N=245V, L2-N=212V, L3-N=239V.
Since the wye primary neutral is not grounded, the 3rd harmonic current component of the transformer magnetizing current is restrained and it may have caused voltage distortion on the secondary L-N due to 3rd harmonic voltages at L-N. This is how I see it, but it would not harm me to consult further.
Another reason can be that the secondary neutral ground is not properly or effectively connected to ground.
Is there any other cause why Line to Neutral Voltage in the secondary side is unbalance?
I always been a fan of having both primary source and transformer primary neutrals grounded. Is it possible to have the Y-y transformer primary and secondary neutral grounded and leave the power source neutral ungrounded ( or a delta primary source)?