I've seen this done many times, but is this method acceptable for installing additional cables to an already full transformer secondary spade bushing?
Bushings_pv19er.jpg
 
Check your cable sizing calculation. 10 cables may be adequate after all, for the rated current.
 
The limiting factor on some of our transformers is the weight of cables putting bending stress on bushing.
 
Thank you jghrist! That's the solution for this application.
 