At transformer, there are tripping relays such as high winding temperature(49T), high oil temp (26Q), rapid pressure rise relay (63FP), main tank presure (63PR), Buchholtz realy (63Q) etc.
What is the traditional way for those relays tripping?
Shall those relays trip the lockout (86) directly or via another device such as the differential protection (SEL-387)?
The drawback of tripping 86 via SEL-387 is that if the relay fails, we also lost all above relay tripping.
If those relays directly trip 86, what if the contact rating (such as, 0.25A@125V DC) of the above relays is lower than 86 coil rating (such as, 4.6A@125V DC)?
Adding an interposing relay will also bring an extra failure point.
Also, if there are two lockouts (86T1, 86T2), shall the differential trip 86T1, and transformer trippng relays trip 86T2, or other?
Thank you for your response.
Best Regards,
Bing