Hi all,
Table 3 IEEE C57.91-2011 indicates
1.5% decrease of load for each 1 Deg C increase in ambient temperature beyond 30 deg C for ONAN and
1% decrease of load for each 1 Deg C increase in ambient temperature beyond 30 deg C for ONAN/ONAF
My interpretation would be say, for a 30 Dg. C rated transformer applied to a 40 Deg C ambient, the total de-rating would be 100% - (10 x 1.5%) = 85%
Therefore, the transformer site rating is = Nameplate kVA at 30 Deg C * 0.85. Is this correct?
My application is here in Canada and I am looking into the CSA C88. However, I seem not to see any standard rated ambient temperature specified there. Are CSA manufactured liquid-immersed power transformers also 30 Deg C ambient rated?
Our Meteorilogical Data specifies 36 Deg C maximum ambient on summer, is it ok to consider 40 Deg C for transformer and cable operating ambient for design purpose?
Thanks
Table 3 IEEE C57.91-2011 indicates
1.5% decrease of load for each 1 Deg C increase in ambient temperature beyond 30 deg C for ONAN and
1% decrease of load for each 1 Deg C increase in ambient temperature beyond 30 deg C for ONAN/ONAF
My interpretation would be say, for a 30 Dg. C rated transformer applied to a 40 Deg C ambient, the total de-rating would be 100% - (10 x 1.5%) = 85%
Therefore, the transformer site rating is = Nameplate kVA at 30 Deg C * 0.85. Is this correct?
My application is here in Canada and I am looking into the CSA C88. However, I seem not to see any standard rated ambient temperature specified there. Are CSA manufactured liquid-immersed power transformers also 30 Deg C ambient rated?
Our Meteorilogical Data specifies 36 Deg C maximum ambient on summer, is it ok to consider 40 Deg C for transformer and cable operating ambient for design purpose?
Thanks