Transformer "Self" Demagnetization

Status
Not open for further replies.

Tstuhl

Electrical
Jun 1, 2018
3
Hello,

I am doing a study on transformer core magnetization and how it plays a role in the transients seen during energization. One of the things that I was tasked with looking into was why some of the transformers that we work with will demagnetize if isolated from the rest of the network (a short is created between all of the bushings and windings and connected to a common ground). The company I am with does not do actual demagnetization of the cores when we isolate them, but we will see that transformers that have been isolated for weeks will experience less severe inrush current upon energization while those that are isolated on the order of days will experience much more severe inrush. Since the peak of inrush current is closely linked to the residual flux of the transformer core, it has lead many of my superiors to conclude that the transformers are demagnetizing, over time, on their own. I am sure there is other, more empirical, evidence that suggests this as well since studies are not ordered for anything.

My question is:
Why would a transformer core demagnetize over the course of a month or more in this scenario?
With my understanding of how to magnetize/demagnetize a ferromagnetic material, you need some kind of energy input to the material, and I am not seeing where this energy would come from other than heat transfer into the core. This, however, seems to be an unlikely explanation. I also did see that there is a demagnetization method that utilizes a capacitor, but I could not find any kind of resource that explained the process or why it would work.
 
Replies continue below

Recommended for you

I found this threads. It answers your questions:

I mentioned that remanence may be a lesser problem than where on the sine curve you Close the breaker. And that is still my opinion. But, for tape-wound ring cores, remanence may be an important factor. Is that what you have?

Re. the capacitor demagnitizion technique, there are recordings at the end of the thread showing how that works.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
When you switch in like Skog said plays a huge role. Point on wave switching is a method that recognizes this. Remenance of the core does decrease over time. The core is not a permanent magnet and heat and the earth's field slowly change the amount of remanence. How quickly it does depends on a lot of things.


------------------------------------------------------------------------------------------