hanksmith
Electrical
- Feb 7, 2008
- 64
Ok,
Have a transformer rated for:
45kVA
Delta-wye
575-208/120
3 phase
I am limited to the use of J type fusing on the line side of this transformer based off Client standards,
Going through the calculations and using the Canadian Electrical code I come up with a 60A J-Type fuse.
When I look at the curves for this fuse I don't think it can handle the magnetizing inrush currents (25 times for 0.01 sec, 12 times for 0.1 sec)
Based off the in rush of this transformer I would need a 80A J-type fuse.
If I put an 80A fuse in the transformer won't be protected for over current, basically the fuse will supply 80A when the transformer should only ever pull 45A max.
What kind of transformer damage would I substain by putting in an 80A fuse and running the transformer at 80A, I would assume it would be very warm and would reduce the life of the transformer. How long could I expect the transformer to hold up like this?
I know this doesn't meet code but just a question on my part.
Any thoughts,
Thanks
Have a transformer rated for:
45kVA
Delta-wye
575-208/120
3 phase
I am limited to the use of J type fusing on the line side of this transformer based off Client standards,
Going through the calculations and using the Canadian Electrical code I come up with a 60A J-Type fuse.
When I look at the curves for this fuse I don't think it can handle the magnetizing inrush currents (25 times for 0.01 sec, 12 times for 0.1 sec)
Based off the in rush of this transformer I would need a 80A J-type fuse.
If I put an 80A fuse in the transformer won't be protected for over current, basically the fuse will supply 80A when the transformer should only ever pull 45A max.
What kind of transformer damage would I substain by putting in an 80A fuse and running the transformer at 80A, I would assume it would be very warm and would reduce the life of the transformer. How long could I expect the transformer to hold up like this?
I know this doesn't meet code but just a question on my part.
Any thoughts,
Thanks