Evening Gents,
Does anyone else find this odd? Am I missing something here?
I'm looking at the Canadian Electrical Code, rule 26-252 (I'll paste the rule in its entirety at the end of this post), which states that I should protect the primary feeders with a circuit breaker rated at up to 300% of the rated primary current of the xformer.
Now if we were to take the example of a 3-phase 300KVA xformer, 4160/600V, then we'd calculate a rated primary current of 41.6A (300000/(4160*1.732)).
CEC rule 26-252 suggests that I can now protect that primary circuit with a 100A circuit breaker. The turns ratio of this xformer is 6.93:1... assuming that something goes wrong on the secondary side and that said secondary sees a current draw of 500A (or that someone gets overzealous and loads up the secondary), then the primary is, theoretically, ony seeing 72A of current (500A/6.93). So what is going to trip that 100A circuit breaker?
Now before anyone jumps too high, I do realize that the primary will see more current than the calculation suggests, due to the heat generated within the xformer, but then would that mean enough extra current on the primary to trip that 100A breaker?
I'm thinking of an example whereby one would want to install a Motor Control Center on the secondary side of this 300KVA xformer, conductors on this secondary would be installed at an ampacity of no less than 395A (500 MCM) (300000/(600*1.732)*1.25), so I'd expect the MCC busses would need to be rated for at least 400A. Here again, the primary fuse would appear to provide inadequate protection. Is there another code rule that would state that a disconnect needs to be installed on the secondary side, or that the primary breaker size needs to be reduced according to the secondary load?
There just has to be more to this.
Any ideas? Thanks.
Oh, almost forgot that rule:
Rule 26-252 Overcurrent Protection for Power and Distribution Transformers Rated Over 750 V
(1) Except as permitted in Subrules (2), (3), and (4), each transformer shall be protected by an individual overcurrent device on the primary side, which shall be rated at not more than 150% of the rated primary current of the transformer in the case of fuses, and which shall be set at not more than 300% of the rated primary current of the transformer in the case of circuit breakers.
(2) Where 150% of the rated primary current of the transformer does not correspond to a standard rating of a fuse, the next higher standard rating shall be permitted.
(3) An individual overcurrent device shall not be required where the feeder or branch circuit overcurrent device provides the protection specified in this Rule.
(4) A transformer having an overcurrent device on the secondary side rated or set at not more than the values in Table 50 or a transformer equipped with co-ordinated thermal overload protection by the manufacturer shall not be required to have an individual overcurrent device on the primary side, provided the primary feeder overcurrent device is rated or set at not more than the values in Table 50.
Does anyone else find this odd? Am I missing something here?
I'm looking at the Canadian Electrical Code, rule 26-252 (I'll paste the rule in its entirety at the end of this post), which states that I should protect the primary feeders with a circuit breaker rated at up to 300% of the rated primary current of the xformer.
Now if we were to take the example of a 3-phase 300KVA xformer, 4160/600V, then we'd calculate a rated primary current of 41.6A (300000/(4160*1.732)).
CEC rule 26-252 suggests that I can now protect that primary circuit with a 100A circuit breaker. The turns ratio of this xformer is 6.93:1... assuming that something goes wrong on the secondary side and that said secondary sees a current draw of 500A (or that someone gets overzealous and loads up the secondary), then the primary is, theoretically, ony seeing 72A of current (500A/6.93). So what is going to trip that 100A circuit breaker?
Now before anyone jumps too high, I do realize that the primary will see more current than the calculation suggests, due to the heat generated within the xformer, but then would that mean enough extra current on the primary to trip that 100A breaker?
I'm thinking of an example whereby one would want to install a Motor Control Center on the secondary side of this 300KVA xformer, conductors on this secondary would be installed at an ampacity of no less than 395A (500 MCM) (300000/(600*1.732)*1.25), so I'd expect the MCC busses would need to be rated for at least 400A. Here again, the primary fuse would appear to provide inadequate protection. Is there another code rule that would state that a disconnect needs to be installed on the secondary side, or that the primary breaker size needs to be reduced according to the secondary load?
There just has to be more to this.
Any ideas? Thanks.
Oh, almost forgot that rule:
Rule 26-252 Overcurrent Protection for Power and Distribution Transformers Rated Over 750 V
(1) Except as permitted in Subrules (2), (3), and (4), each transformer shall be protected by an individual overcurrent device on the primary side, which shall be rated at not more than 150% of the rated primary current of the transformer in the case of fuses, and which shall be set at not more than 300% of the rated primary current of the transformer in the case of circuit breakers.
(2) Where 150% of the rated primary current of the transformer does not correspond to a standard rating of a fuse, the next higher standard rating shall be permitted.
(3) An individual overcurrent device shall not be required where the feeder or branch circuit overcurrent device provides the protection specified in this Rule.
(4) A transformer having an overcurrent device on the secondary side rated or set at not more than the values in Table 50 or a transformer equipped with co-ordinated thermal overload protection by the manufacturer shall not be required to have an individual overcurrent device on the primary side, provided the primary feeder overcurrent device is rated or set at not more than the values in Table 50.