MurrayBall
Electrical
- Aug 24, 2005
- 7
Transformer: 3750kVA
Primary: 12.47kV Wye solidly grounded(connected to the utility line).
Secondary: 2400V Delta
Experiencing occasional 51N trips, that is, primary neutral current. 51N relay picks up at 2.0A.
51N current all the time about 1.0A; with 300:5A CTs equates to 60A primary.
One time even experienced a trip with no load on the secondary.
Disconnected primary H0 bushing from ground which caused the 51N current to go to zero.
Transformer tests okay.
Any ideas as to where the problem lies?