Can I operate two transformers; 3MVA 440 Volts, 50 Hz, 6% impedance and 4MVA 440volts, 50Hz, 7% impedance; in parallel?
If yes what will be the percentage load sharing by each of them?
 
Replies continue below

Recommended for you

Forgot to mention that vector group is same for both of them.
 
Hi.
Usually, recommended 10% difference between Uk%.

possible check oveload and undeload situation.
according:
Uk% for both=(3+4)/( 3/6+ 4/7)=6.54%

S1=3x6.54/6=3.28
S2=4x6.54/7=3.72


 
Normalize the impedances. The 4 MVA will derate to 3.43 MVA at 6% impedance. Total load may be 6.43 MVA and the transformers will share the load in proportion to their normalized MVA ratings (3 MVA and 3.43 MVA).
If the X/R ratios are not equal the total allowable load will be less than 6.43 MVA.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
I did an "exact" calculation and the result is not far from the results in above posts.
The load will be shared depending- but only a bit- on load pf. If 440 V is the rated transformer voltage the Load voltage will be less due to the drop voltage on transformers.
For instance if the rated Load Sload= 7 MVA and pf=0.8 then S1=3.125 and S2=3.57 MVA. But if pf=0.9 then S1=3.154 MVA and S2=3.604 MVA.
 