A third world trasformer re manufacturer has built me an 25kw/28kva 3ph oil filled, convection air cooled, distribution transformer. I would like to put 38kva through it occasionally for 50% 10 min. cycles lasting one hour twice a day but I an planning to manage the load to the limit of the transformer.
If the transformer lives for only one year then I would be happy but I am not in a position to monitor the oil with an instrument to evaluate it's health.
the ambient is 20 deg. C but the name plate does not refer to that. I have a fan and an oil thermometer installed and it is pole mounted and I own the hydro plant.
I want to overload this safely. the only load is a motor with a power factor of 0.87 and i have a 5kva capacitor bank that I can trim back to the correct value. the compressor cycles between 25hp and 45hp.
I would like to target a capacitance to give me a 1.0 Pf at the offloaded 25Hp if this is safe for the equipment.
Following is an interesting comment from the pump forum from where the this thread began.
waross (Electrical)
29 Mar 09 19:36
Transformer capacity is based on self heating at the maximum rated ambient conditions. If you have an ambient significantly lower than the design ambient, (and many installations do), the actual overload based on temperature rise may be less than 15%. When a step increase in load is applied to a transformer it takes about 15 minutes for the transformer to respond thermally (reach a new, higher temperature). Transformers will often accept an overload with only a reduction in service life, but the reduced life may be many years.
Many transformers may be re-rated with the addition of external cooling.
The best approach may be to contact the transformer manufacturer and ask for recommendations for increasing the rating with increased cooling. This will avoid code violations.
An alternate is to compare the actual ambient to the rated ambient to see if the transformer is in fact overloaded. I would take this question to the electric power forum. Have accurate figures fr the rated ambient of the transformer and the actual ambient. Note, this approach may result in a code violation even if the transformer is safe.
If the transformer lives for only one year then I would be happy but I am not in a position to monitor the oil with an instrument to evaluate it's health.
the ambient is 20 deg. C but the name plate does not refer to that. I have a fan and an oil thermometer installed and it is pole mounted and I own the hydro plant.
I want to overload this safely. the only load is a motor with a power factor of 0.87 and i have a 5kva capacitor bank that I can trim back to the correct value. the compressor cycles between 25hp and 45hp.
I would like to target a capacitance to give me a 1.0 Pf at the offloaded 25Hp if this is safe for the equipment.
Following is an interesting comment from the pump forum from where the this thread began.
waross (Electrical)
29 Mar 09 19:36
Transformer capacity is based on self heating at the maximum rated ambient conditions. If you have an ambient significantly lower than the design ambient, (and many installations do), the actual overload based on temperature rise may be less than 15%. When a step increase in load is applied to a transformer it takes about 15 minutes for the transformer to respond thermally (reach a new, higher temperature). Transformers will often accept an overload with only a reduction in service life, but the reduced life may be many years.
Many transformers may be re-rated with the addition of external cooling.
The best approach may be to contact the transformer manufacturer and ask for recommendations for increasing the rating with increased cooling. This will avoid code violations.
An alternate is to compare the actual ambient to the rated ambient to see if the transformer is in fact overloaded. I would take this question to the electric power forum. Have accurate figures fr the rated ambient of the transformer and the actual ambient. Note, this approach may result in a code violation even if the transformer is safe.