Hi
The insurance requests to do tansformer oil testing yearly.
Should we do same for hermetically sealed transformer and transformer with DGPT?
 
These models do not have a conservator.
 
Hermetically sealed transformers do not require yearly testing unlike the conservator transformers. These are not designed for oil top up that easily and better to take samples only if & when required.
You can approach the manufacturer and the insurance authority for the periodicity with hermetically sealed transformers.
 
SAO7
Hermetically Sealed Oil Filled Transformer has an oil drain tap to take oil samples annually as per Mines statutory requirements (RSA)
 