We have a 10/12.5MVA sealed transformer operating at 13.8 - 4.16kV and our recent oil tests gave "unacceptable" results for the power factor. The transformer consistently has a positive pressure nitrogen blanket on it, approximately 3-5 psig. I think it is very unlikely that water is the culprit and I don't believe the unit has been ridden hard. Normal load is well under 50% of nameplate.
The Liquid Power Factor history on this transformer is as follows:
Date 25C 100c
4/18/00 .072% Acceptable 1.916% Acceptable
6/6/01 .046% Acceptable 3.182% Questionable
6/29/02 .154% Questionable 3.410% Questionable
6/4/03 .239% Questionable 5.336% Unacceptable
As I am not familiar with the liquid power factor, I cannot think of what is causing the problem and what to do about it. Perhaps this isn't a serious problem. I have not asked the oil testing company about it but their written report says that this test is meaningful in determining the aging and life expectancy. Any thoughts? Suggestions? Warnings?
Date 25C 100c