Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Transformer Noise

Status
Not open for further replies.

EEuno

Electrical
Oct 23, 2007
10
I have a noisy dry type, 75KVA step down transformer. Does anyone know at what distance from the transformer a proper sound measurement is to be made to insure compliance with ST20 specifications?
 
Replies continue below

Recommended for you

There's kind of a lot to it. But in summary, for your 75kva, you need to make measurements at 3 foot intervals around the unit at elevation of half it's height. The instrument should be one foot from the "sound producing surface" but there can be no less than 4 readings located in the 3 foot increments. There's also a table to correct for ambient noise.



Neil
 