Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations 3DDave on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Transformer magnetizing inrush current

Status
Not open for further replies.

IndianTechEngg1001

Electrical
Mar 22, 2010
81
What is the ingredients of transformer magnetizing inrush current in terms of +ve, -ve and zero seq currents?
 
Replies continue below

Recommended for you

Transformer inrush is highly non-sinusoidal (lots of harmonics).

+/-/0 sequence describes only one frequency (for example fundamental).

If wye connected, no zero sequence. Whether the fundamental contains unbalance and negative sequence, I’m not sure.

Typically as you know inrush is discriminated from through fault on the basis of harmonic content.


=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
electricpete said:
If wye connected, no zero sequence.
You might be closer to the truth if you said for delta connected, but even then relays will see residual current in transformer inrush.
 
I meant ungrounded wye.

Residual current considers all frequencies, zero sequence applies to only one frequency and I had in mind the fundamental. I believe there will be no fundamental zero sequence in ungrounded wye. (If I'm wrong I'm sure someone will let me know). Residual current clearly will be more relevant for relaying....I'm not sure what the OP is after when asking about sequence content.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
With an ungrounded primary winding, there will be no zero-sequence current in the winding. There may be a small amount of zero-seq current in CT secondaries if there are CT errors.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor