traj123

Electrical
Jun 14, 2013
1
Hi all,

Is it possible to calculate/ make an educated guess about iron and copper losses from the following information:

1) Transformer ratings: 20MVA (34.5kV -> 70kV)
2) %z = 10% impedance at base
3) X/R = 23

I need to make some preliminary assessments and I'm not a power systems engineer so I'm lost. Thanks for the help!!!
 
Replies continue below

Recommended for you

You have Z and X/R, so this will give you the load (copper) loss.

Z^2 = R^2 + X^2

= R^2 [ 1 + (X/R)^2 ]

So, taking sqrt and rearranging, you get

R = Z / SQRT[ 1 + X/R)^2 ]

Now Z in ohms can be derived from your %Z and the base ohms.

Base ohms = kV^2 / MVA or 34.5 * 34.5 / 20 if you are looking at the 34.5 kV side

Zpu = 0.10

Z(ohms) = Zpu * Base ohms

Plug and chug


You won't be able to estimate the iron or core losses from what you've provided.
 
You have to add 10-20% more to I2R to get load loss to take in to account the eddy loss in winding and stray losses in metal parts.
 
Hi Magoo2,

From your equation, it seems that the whole result will change based on "if" the primary or secondary voltage is chosen.

What is the actual rule please?

Thanks.
 
Hey AustLee

It depends on what you're using the results for. As you said, you'll get a different result if you base it on 34.6 kV than you will if you do it for 70 kV.
 
The losses (in watts) are the losses. If you're getting different losses when calculating from the primary side and secondary side, there is an error in the calculation method.
 
DPC is correct. I was thinking in terms of base ohms and not losses. My mistake.
 
Ok so what is the correct formula then, as the value of the losses in the above equation will vary depending on the voltage used
 
Losses don't changed when voltage changes. Z base changes when voltage changes, ohms change when voltage changes. Current changes when voltage changes. But losses are independent of which side "supplies" the losses.
 
I agree with prc if the X/R value is "calculated " and not measured. I think if it is measured –at the steady state [100% load] in the rated ambient, it has to include the eddy current and stray losses[ except iron core losses]. Usually the"R" losses are extracted from load losses and no-load losses.
As per IEC 60076-8 ch.7.2
"The test permits separation of the series impedance into a resistance, representing the load loss, and a reactance:
Z = R + jX "
As per IEC 60076-1
ch.10.4 Measurement of short-circuit impedance and load loss:
"the a.c. resistance derived from the load loss"
 