Sep 25, 2008 #1 Humble2000 Electrical Joined Nov 17, 2005 Messages 132 Location CA If the main secondary breaker has ground fault protection, do we still have to protect the transformer shifted curve on delta-solidly grounded wye transformer against phase-ground faults which is shifted to the left?
If the main secondary breaker has ground fault protection, do we still have to protect the transformer shifted curve on delta-solidly grounded wye transformer against phase-ground faults which is shifted to the left?
Sep 25, 2008 #2 jghrist Electrical Joined Jul 16, 2002 Messages 4,226 Location US You have to protect for a ground fault on the source side of the main secondary breaker. Upvote 0 Downvote
Sep 25, 2008 Thread starter #3 Humble2000 Electrical Joined Nov 17, 2005 Messages 132 Location CA Thank you! Upvote 0 Downvote