Hello Gentlemen,
I am a new comer for this forum. I saw this thread on transformer impedance change, but decided to not to comment, as I also cannot agree in anyway with the so called “impedance test” and also due to the fact that JWILSON3 has not witnessed such an important test.
Since YENRAMESHN had pushed this posting to a different way and made some comments on the zero sequence current components, which has no relevance to this thread as he himself says, I too got some interest to get involved.
YENRAMESHN
I cannot agree with your comment on May 23 rd which says “ For a zero sequence current to flow in the secondary winding, the star point (neutral point) has to be grounded”. IT IS NOT NECESSARILY TO BE. If there is a 4 th conductor on a three phase system then zero sequence components will exit. In that way JGHRIST is fully correct and I agree with his immediate reply on May 23 rd. Load side of a Delta/Star transformer is not grounded. Then how do you analyze a Phase to neutral fault ( X1 to X0)on the load side using sym. components where zero seq. components are involved in the calculation? In a 3-phase 4-wire distribution system if a fault occurred between a phase and the neutral, will the residual earth fault protection (51N) or zero sequence protection (51GS) scheme respond? The answer is No. The transformer will trip from overcurrent (50/51) and not from any of the ground fault schemes (51N or 50GS). The reason is that the zero sequence currents DO exist but they are balanced by the 3I0 flowing in the neutral which is the 4 th conductor. Similarly, take a 30 A, 3 phase, 4-wire household ELCB (RCCB) and if we bridge one phase and the neutral terminals using a test lamp, it will not trip on earth leakage but depending on the fault the main or branch MCCB/MCB will trip on overcurrent. Same thing will happen for a single phase RCCB too. But if we bridge a phase terminal and “ground”, then definitely it will trip. Reason is even though the zero sequence currents DO exist in the first case they are all balanced in all 4 conductors. Nothing exist in the earth path. In the second case, yes they DO exist and flow in the earth return path, but this time nothing in the earth path. I hope this will help you to think about it again.
JWILSON3
With regard to impedance change, I can reasonably claim that the manufacturer had done a test which is not correct neither as per ANSI/IEEE C57.12.90 nor per IEC 76. Normally the impedance test is done along with the test for load losses so that we can estimate transformer load losses too. If we are doing the impedance test
1)Using a three phase supply then a VARIABLE 3-phase supply has to be connected to H1, H2 & H3 while short circuiting X1, X2 & X3. (no connection with X0). Supply is raised till we get the primary current equal to 138 Amps corresponds to 3 MVA (AA rating) and not to 5 MVA(AFA) and then to be corrected to 75 deg C for accurate results to compare with original test results.
2)Using a single phase supply then it has to be connected to H1 (H2 or H3) while H2(H3 or H1) is earthed while short circuiting X1, X2 & X3. (no relevance with X0). Supply is raised till we get the primary current equal to 138 Amps correspond to 3 MVA (AA rating) and not to 5 MVA(AFA) and then to be corrected to 75 deg C for accurate results to compare with original test results.
As far as I know this is the standard routine test suitable for measuring the impedance voltage irrespective of whether the secondary is delta or star. That means, for your
3/ 5 MVA(AA/AFA) dry type transformer having a primary rated voltage of 12470 Volts with a name plate impedance of 6.07%, we should apply at least 756 Volts to the primary so that 138 Amps is flowing in the primary while X1,X2,X3 terminals are short circuited. Therefore the results of 27.41 V. 3.0 Amps, 135.4 Amps does not sound good for me.
Since the manufacturer has not followed the standard method, I think before any replacement you should ask them to repeat the test so that you also can witness. If all the other routine tests ( specified by NETA-MTS-2002) are OK and if the impedance test results is then become “SENSIBLE”, my advice is to energize the transformer without a second thought.
Regards!