Feb 28, 2017 #1 hallmg Electrical Joined Aug 12, 2016 Messages 19 Location GB Hello, The query i have is when performing isolations on transformers, why is the transformer secondary breaker opened first? Any help would be much appreciated. Regards, Hallmg.
Hello, The query i have is when performing isolations on transformers, why is the transformer secondary breaker opened first? Any help would be much appreciated. Regards, Hallmg.
Feb 28, 2017 #2 ppedUK Electrical Joined Jul 8, 2009 Messages 94 Location GB Mainly to prevent any back-feeds from the LV system appearing on the HV "Circuit" side when carrying out the HV isolation. Upvote 0 Downvote
Mainly to prevent any back-feeds from the LV system appearing on the HV "Circuit" side when carrying out the HV isolation.
Feb 28, 2017 Moderator #3 waross Electrical Staff member Joined Jan 7, 2006 Messages 28,651 Location CA Opening the secondary first take the load off the transformer so the primary breaker has only to interrupt no-load current. Bill -------------------- "Why not the best?" Jimmy Carter Upvote 0 Downvote
Opening the secondary first take the load off the transformer so the primary breaker has only to interrupt no-load current. Bill -------------------- "Why not the best?" Jimmy Carter
Mar 1, 2017 Thread starter #4 hallmg Electrical Joined Aug 12, 2016 Messages 19 Location GB Hi, Thank you very much for the advice. Hallmg. Upvote 0 Downvote