Hi Bronzeado,
The event that occurred was a bit more complex than what I described in my previous email.
The setup basically consists of a number of generators connected to a common 33 kV busbar by means of star delta transformers (Star winding is on the 33 kV side, with a solid connection to ground).
For an unknown reason, Generator no 3 issued a trip signal, and its transformer was disconnected from the 33 kV busbar by its 33 kV ciruit breaker.
The protection on Generator transformer 5 detected a current flowing to ground from its star point, and due to a fault in the connection of the restricted earth fault relay, issued a trip command to the 33 kV circuit breaker of Generator transformer no 5. (We now know that an inverted CT caused the maloperation of the restricted earth fault relay of Generator transformer no 5).
From the waveforms attached, you can see that two current pulses were recorded on the connection of the star point of generator transformer no 5 to ground (yellow curve). These correspond to the tripping of first Generator 3, and then Generator 5. My original question was about why there should have been a current to ground, when all that happened was an opening of a circuit breaker.
I have also attached a sketch I made of the flow of current in the sequence networks (connected in parallel, assuming that one pole of the circuit breaker opened while the other two were still closed). This explains the presence of a zero sequence current in the star point connection of both the disconnecting transformer and the remaining transformers in the system (only one shown in my sketch).
It also shows that the zero sequence current in the disconnecting transformer and that in the remaining transformers should be 180 degrees out of phase.
I expected to see this phase shift of 180 degrees between the two phasor diagrams, as for the LHS diagram, Generator transformer 5 was one of the remaining transformers, while for the RHS diagram, Generator 5 was the disconnecting transformer.
However, the diagram shows approximately 60 degrees of phase shift. This can be explained if a different pole first interrupted the current in each of the two cases, as this phenomenon would introduce a 120 degree phase shift (180 - 120 = 60).
Unfortunately I do not have the software to model a single phase open circuit ffault, so I cannot confirm my interpretation of the results.
Best regards,
Alan
PS Waveform file is in the next post