Well I was back at work today so I went digging for some more info to shed light on whether or not the resistance controls the inrush (for an example generator stepup transformer, not necessarily representative of others)
Attached is some info from one of our Generator Stepup Transformers.
One document is the
ratings
362.25kv/25kv wye/delta
850MVA
Rated HV current 1426
On-load losses 1629kw
If we compute an efficiency as 1-(1629kw/850mva) it is something like 99.8% efficient.
If we had no other info and tried to estimate conservatively high estimate of winding resistance, we might assume 100% of the losses come from the HV winding I^2*R (in fact there is also LV winding I^2*R, core losses, stray losses).
A HIGH estimate for HV winding phase to neutral resistance would be
R = Losses / (3*I^2) = 1,629,000W/(3*1426A^2) = 0.27 ohms
If resistance controls the peak current, what would the peak inrush current be?
I = sqrt2*(V/sqrt3) / R = sqrt2*209,145v/0.27 = 1,095,466A which is 476 times as high as the peak rated current sqrt2*1426A
In fact when measured directly during a test at room temperature the HV winding resistance phase to neutral was 0.11 ohms per
second attachment(maybe a little higher at operating temperature). So if resistance controlled the current then the previous result would easily double to something like 1000 times rated current.
That does not compute for me for a number of reasons. For one I've never heard anyone mention a multiple anywhere near that high (I've heard numbers up to 40x rated). For another thing I’d think our waveforms would have shown obvious evidence of CT saturation but the waveforms I remember from inrush were somewhat smooth for most of the waveform (I wasn’t able to track down any waveforms… wish I would have been better at saving stuff). Also the transformer and incoming lines would heat quite a bit. For a third thing I’d wonder how those big long HV bushings could stand the forces (I realize they are well separated but they would also interact with tremendous induced circulting currents in the tank).
Another thing to consider aside from the high magnitude is the dc component which lasts for a long time (10 or 20 seconds = 600 or 1200 cycles). It seems to iondicate that inductance remains relevant in the circuit (you’d think resistive controlled circuit would decay a lot quicker).
With all that said I still don’t have a good explanation for how the magnetics controls the current when pushed so far into saturation. The best I can come up with is that it is well beyond the linear limit for saturation but not so far that it acts like an air core . Also my simple thinking involved single phase transformer, there may be complications when we think about the different legs of the core and how this interacts with the other phases that I’m not understanding. More questions than answers. I am happy to leave it an open question.
=====================================
(2B)+(2B)' ?