Can anyone point me to an IEEE or ANSI standard that addresses the maximum variation in transformer impedance for a three-phase delta connected bank? I cannot seem to find a definitive answer, but rather some generalities (such as + or - 7.5%).
I have a client who recently lost two transformers (due to a secondary bus fault) and is in need of getting two replacement single-phase transformers. The problems are; immediate delivery; and matching the existing 2.0%Z. I have located two transformer with 1.9%Z and 2.1%Z. Will the 1.9%Z unit have to be de-rated due to a 10% difference between the two new units?
I have a client who recently lost two transformers (due to a secondary bus fault) and is in need of getting two replacement single-phase transformers. The problems are; immediate delivery; and matching the existing 2.0%Z. I have located two transformer with 1.9%Z and 2.1%Z. Will the 1.9%Z unit have to be de-rated due to a 10% difference between the two new units?