I'm trying to determine the appropriate way to represent 3-winding Delta transformer to its equivalent Wye representation. The given data were: Primary : Secondary voltages, its MVA rating, MW loss, and %Z. I saw an old note in the past which indicates the calculated resistance as %R = MW loss * 100 / rated MVA. I didn't see any logic in this resistance calculation. If you have any links or advices to the above subject, please let me know. Thanks.
The formula you gave is more understandable if you write it as:
%R = I^2 R * 100 / (I^2 Z)
I^2 * R = the resistive losses
I^2 * Z = MVA rating
Expressing the losses as a % of the MVA rating is what the formula does. It is common to all transformers - be they 2 winding, 3 winding or more.
A test report should give you the %Z between pairs of windings. With a 3 winding transformer, let's call the terminals H, L and T (high, low and tertiary).
Get 3 values from test report:
Z_H-L = impedance between H and L
Z_H-T = impedance between H and T
Z_L-T = impedance between L and T
Z_H = 1/2 (Z_H-L + Z_H-T - Z_L-T)
Z_L = 1/2 (Z_H-L + Z_L-T - Z_H-T)
Z_H = 1/2 (Z_H-T + Z_L-T - Z_H-L)
Looks better if you can use subscripts, but this should give you what you want. These impedances, Z_H, Z_L and Z_T are the wye equivalent values.
Magoo2,
Truly appreciate for your help. Have a great day.
One more question. What is the difference between the above Delta-Wye conversion and that of the typical formula: Z_H = (Z_H-L * Z_H-T)/ Z_sum, where Z_sum = Z_H-L + Z_H-T + Z_L-T ? I'm trying to facilitate the equations above with full representation of Z = R + jX and compare with the one you gave, but have a tough time of seeing the corresponding relationship. Thanks for any help.