@cranky108 - yes it is the H0 bushing I am talking about and thank you.
@argotier - this is interesting and likely why it was done since there are multiple transformers in parallel with the H0 ungrounded but a surge arrester connected to the H0 terminals.
Essentially what you both are saying is that my H1, H2, H3 bushings, H winding, and H0 bushing should have all the same BIL rating, say 900 kV. What about adding the surge arrester to the H0 terminals, can we consider reducing the insulation level of this bushing? What does adding a buried delta tertiary winding do?
Thanks!