I am working on a foundation design for a transformer to be used in a substation. I am given a vertical load and told the height of the transformer. This transformer does not have an oil spilled containment, it is just a rectangular slab. I have been given initial dimensions for the transformer foundation slab. I have designed transformers in the past for refineries, but this is my first time doing it for a substation. I believe it should be designed the same way. Is that assumption correct?
When previously designing transformer foundations, the information I first obtained was: the erection & operating weight of the transformer, plan dimension of transformer base, height of transformer, center of gravity location when dealing with seismic, and anchor bolt size & location. The geotechnical information I used was the soil allowable bearing pressure, soil density, and ground water table location.
I computed my lateral shear load and moment caused by wind and/or seismic loads, then checked for the soil bearing pressure, sliding & overturning stability. After determining that the size of my foundation was adequate, I designed the the slab as a regular one-way slab based on the applied forces for strength. Then I designed/checked my anchor bolts.
I was asked about the considering 2/3 dimensions of the slab, dealing with eccentricity, and considering the center of gravity. Some of these other checks seem unfamiliar. The transformer is not in a seismic area, so I am not sure the need for center of gravity (I can assume the center of gravity based on the foot print of the transformer since I don't have vendor drawings).
Please let my know if you see something I am missing/overlooking. Any suggestions/comments are appreciated.
When previously designing transformer foundations, the information I first obtained was: the erection & operating weight of the transformer, plan dimension of transformer base, height of transformer, center of gravity location when dealing with seismic, and anchor bolt size & location. The geotechnical information I used was the soil allowable bearing pressure, soil density, and ground water table location.
I computed my lateral shear load and moment caused by wind and/or seismic loads, then checked for the soil bearing pressure, sliding & overturning stability. After determining that the size of my foundation was adequate, I designed the the slab as a regular one-way slab based on the applied forces for strength. Then I designed/checked my anchor bolts.
I was asked about the considering 2/3 dimensions of the slab, dealing with eccentricity, and considering the center of gravity. Some of these other checks seem unfamiliar. The transformer is not in a seismic area, so I am not sure the need for center of gravity (I can assume the center of gravity based on the foot print of the transformer since I don't have vendor drawings).
Please let my know if you see something I am missing/overlooking. Any suggestions/comments are appreciated.