Transformer fault current calculator

Status
Not open for further replies.

linemanager

Electrical
Joined
Feb 19, 2005
Messages
2
Location
US
Transformer fault current calculator

I’m looking for a fault calculator to download (buy) to calculate standard utility transformers such as 667KVA 7200/12470- 277 V 3%Z transformers single or three phase
Any info would be welcomed
 
You could setup a spreadsheet that calculates those quantities pretty quickly using the "infinite bus" method.

Mike
 
Assuming infinity bus, which you should for utility xfrms,
the formula can't get any simpler.

Max. SCC in amps for a xfmr =FLA/Z
where Z is in per unit. (3%=.03pu)

You can set up a spreadsheet for this calculation.

In fact it takes less time to calculate it on a calculator, then the time it takes to open a excel program on a PC!!







 
What is your e-mail address? I have the program written in Visual Basic. I can e-mail it to you.