Hi prc,
I've now obtained copy of C.57-142 2010.
I see it states "Users of switching devices switching transformers that are inductively loaded (that is reactor loads, or
stalled or accelerating motors) or those operated on a frequent basis (daily or weekly) should strongly
consider transient mitigation means (see [B39], [B43]– [B45],and [B48])
B39 being a paper for surge limiters for VCB.
I don't have that paper, but as mentioned in earlier post we do have surge arrester at the MV switchboard.
I do note the point of the author's though that internal transformer insulation may well be overstressed when oscillatory voltage is applied at the winding terminal. And that they recommend also to protect transformer with dedicated surge arrester as IEEE Std 62.22
Your point you make about always using the pre-mag circuit we have , so we reduce the probability of interruption of higher inrush currents that would lead to these oscillatory voltages correct??
So if i have understood generally (as i have not digested it fully), the point about regularly energisation of your dry type transformer is not so much the energisation itself but rather the interruption on load (or no load) when taking transformer offline and also possibility of VCB contact bounce/contact gap transients on closing when bringing transformer back on line, and in each case the possibility to set up oscillatory voltages internally in transformer.
The pre-mag circuit itself only being of some benefit if a VCB trip condition were to occur during energisation, the pre-mag circuit is not a mitigation itself to this phenomena, only some form of safe guard each time transformer is energised.
Only real safe guard against this failure when considering need for frequency energisation would be use of RC snubber at transformer or otherwise pre-insertion resistors to damp the transient wave. One would not specify pre-mag transformer as a solution to frequent energisation.
Have i understood that correct.