It’s a ship’s distribution transformer. 6.6/0.45kv, feeds general ships loads. Part of redundant pair, one feeds port bus, the other starboard bus. so typically each transformer carries less than 50% load. If one transformer were to fail, other could supply both port and starboard bus loads.
Typical ships loads, pumps, fans, domestic loads etc supplied.
I don’t think it is a power quality related thing. There is a pre-mag solution employed for energising transformer on weak grid. Transformer rated 3.5MVA. Generator plant on 6.6kV are four diesel, 2x 2.75MW and 2x4MVA sets. The pre-mag solution allows transformer to energise from single generator following a black out.
Interlocking on mv and lv sides, so transformer will be energised on no load. Then lv breaker closes (either on dead bus, or part of auto-transfer scheme to redundant transformer)
Ship staff find the time restriction very prohibitive as it stands, e.g they may transfer loads to one transformer. Then they have this 12hr operating restriction before they can swing loads back again on to the other transformer. This is not a daily occurrence, e.g. for maintenance on LV switchboard or transformer, or occasional switchboard training drills. They want to ditch the 12hr restriction that nobody seems to understand where it crept in.