ThePunisher
Hi all,
We have experienced recently a strange percentage differential trip while starting a motor downstream. The GE Multilin T60 is installed to protect a 1 MVA, 7.2-0.60 kV power transformer. The differential CT inputs are 400:5A at the transformer's primary 7.2 kV bushing and 1200:5A secondary CT located load side of the downstream 600 V main circuit breaker of MCC. The differential P/U is 0.30 p.u., Slope 1 = 25%, Break Point 1 = 2 p.u., Break point 2 = 8 p.u., Slope 2 = 80%
The transformer was successfully energized and undergone a 24 hours no-load operation (Soaking).
After 2 days, a 30 HP, 575 V induction motor is started (bump-testing) at the 600 V MCC and it tripped the percentage differential at an Idiff event measured at 0.69 p.u.
This somewhat puzzles us as the current flow is unidirectional and if there are harmonics, the relay's harmonic inhibit was enabled and don't think it would go to a Idiff pickup as high as 0.69 p.u.
Did anyone had the same issues in the past? If yes, how did you mitigate it? If none, what do you think is the problem.
We checked CT polarities and system set-up in the relay ans they are all fine.