Hi,
We have a transformer delta-delta configuration with differential protection.
The CT on the secondary side of the transformer are in the delta of the transformer, so the current measured isn't the same as the line current.
I've made a sketch if it's not clear.
So i want to know to do accurate differential protection with these ct, since the current in the delta is not the line current. We know that current in delta will be the line current divide by 1.73 with a angle of +30 deg vs the line current.
Is it better to add CT somewhere else? We can put CT in the switchgear that is 500 ft away, so the differential protection will aso take the cables.
Thanks