Since we don't know a lot of data we have to use our experience proposing these [as odlanor did].
The required data could be [developing a little the modest list of odlanor]:
System short-circuit apparent power Ssys and system R/X-as jkristinn said.
If the maximum [usually] breaker rated current is 50 kA [rms] the Ssys=sqrt(3)*34.5*50= 3000 MVA [approx.]
Let’s say Ssys=3000 MVA at 34.5 kV and X/R=10.
Recalculating at 13.8 kV Zsys=13.8^2/3000= 0.06348 ohms and Xsys=sqrt[Zsys^2/(1+1/100)]= 0.063165 ohm and Rsys=0.0063165 ohms.
Now we shall appreciate the short-circuit impedance zk% and pcu% copper losses in the transformer. Let’s say zk=8% [in order to limit the short-circuit current at 25.1 kA if Sys=infinite.]and pcu=0.5%.
ZT=8%*13.8^2/75=0.203 ohm RT=0.5%*13.8^2/75=0.0127 ohm and XT= 0.2027
Also, let's say the steady state load power factor- before motor start- was 0.75 [in order to cover 75 MVA from 50 MW “declared” load and Smot at steady state].
Let's say the starting power factor of the motor was 0.15 [I think 0.4 is too high odlanor!
![[pipe] [pipe] [pipe]](/data/assets/smilies/pipe.gif)
]. Starting current will be 7 times the rated current of motor at rated voltage [Nevertheless the modern class D could be 4.5 kVA/HP=3 times, may be].
If we put as total active power-when starting- P=50+SQRT(3)*13.8*0.351*7*0.15= 58.8 MVA and total S=50/0.75+SQRT(3)*13.8*0.351*7=125.4 we get cos(fi)=P/S=0.469 then fi=1.0826 radians.
For System drop we use the IEEE Standard 141 VOLTAGE CONSIDERATION –the approximate formula: V=I*R*cos(fi)+I*X*sin(fi) and neglecting the supplementary angle introduced by transformer impedance fi=1.0826 radians.
DUsys=sqrt(3)* 125.4 /sqrt(3)/13.8*[(0.0063165 *cos(fi)+ 0.063165 *sin(fi)]=0.5334 kV
U2o=13.95-0.5334=13.42 kV
Using the way proposed by prc [See thread238-221175 VOLTAGE DROP AT XFMR)
according to IEC 60076-8 clause 7.4 The voltage drop equations :
A=S/U2^2*[XT*sin(fi)+RT*cos(fi)]
B=S/U2^2*[XT*cos(fi)-RT*sin(fi)]
DU2=U2o*(A-A^2+B^2/2...) –neglecting ....[of course!].
S=125.4 MVA U2o=13.42 kV
Recurrently-replacing U2 updated in A and B- we get finally:
A= 0.173807 B= 0.085796 DU2=11.45*(0.173807 -0.173807 ^2+0.085796 ^2/2)= 1.9765 kV.
Then total voltage drop at transformer terminals will be 13.8-11.45=2.35 kV[17%].
For a more accurate result we have to refer also to the tap position [if any].
Let's say between motor and the compressor is a clutch and the motor will start without any load [only J of the motor will be taken into consideration in order to calculate the starting time].
Let’s say the no of poles=8 freq=60 Hz rpm=3600/4=900 .
Calculated motor rotor diameter will be 1.5 m and the ideal length 0.9 m then the mass of the rotor will be 12900 kgf. In this case GD^2=kgf*dia^2/4=12900*1.5^2/4=7256 kg.m^2 [approx.6*7256=43540 lbs*ft^2].Let’s say no load torque will act against the motor so the accelerating torque will be approx Tacc=2*Tfl. [Tfl = Php 5,252 / ωmax wmax=2*pi()*rpm
Tfl=7.5*746*5252/2/pi()/900 =5196.4 lbs.ft
tstart=wk^2*(ωmax -0)/Tacc/308=5196.4*2*pi()*900/2/5196.4/308 =9.18 sec.
The transformer has to withstand 9.18 sec 125.4 MVA [125.4/75=167.2%].I think it is not a problem.