I don't know what code you are working under.
In North America, we are bound by the Canadian Electrical Code or by the National Electric Code.
1. Electrical equipment in general must be used withing the approved ratings. Transformers must be rated to carry the calculated load.
Our issue is the Calculated Load.
(3) The calculated load in a consumer’s service, feeder, or branch circuit shall be considered a continuous load
unless it can be shown that in normal operation it will not persist for
(a) a total of more than 1 h in any two-hour period if the load does not exceed 225 A; or
(b) a total of more than 3 h in any six-hour period if the load exceeds 225 A.
(4) A load of a cyclic or intermittent nature shall be classified as continuous unless it meets the requirements
of Subrule (3).
Also, when loads are mutually exclusive such as electric heating and electric air conditioning, only the greatest need be considered.
I have mentioned an exception for additional loads when it is shown that the demand over a period of time justifies a lesser demand.
In a hypothetical case:
You are designing similar or identical pumping stations.
You are designing a new station and you have historical data from existing pumping stations that demonstrates that a lesser demand factor is justified.
If you came to me as the AHJ and asked for an exception to the rules based on available data, I would be inclined to grant an exception subject to the following conditions.
1. My ability under the local code to grant an exception.
2. Assurances that the flow, density, pressure difference and loading of the proposed station will be equal to or less than the conditions of loading of the example stations.
3. Any exemption will be based on information supplied by yourself and you will be solely responsible if there are future issues with the installation and the AHJ will be held blameless.
Bill
--------------------