In medium voltage distribution networks there is a 3 wires coming from substation transformer with Delta secondary connection, and there's a grounding transformer which is used to create a neutral point which we connect it to ground to create a ground path to detect ground faults,now before we connect that neutral point to ground,we have ungrounded system and there is no meaning of phase to ground voltage, is it right? As if I measured voltage between any line and ground there will be no reading and if any one touch any line while touching ground he will not get a shock as if there isn't any other fault,is it right? But after grounding the neutral point , the. The voltage between any line and ground will be 11/sqr(3)=6.4kv , is it right? Now ,
First question can we use 6.6 kv insulators instead of 11kv insulators while neutral point is grounded?
2) the medium voltage indicator, how it works? Does it depends on the ground as reference meaning when choosing a voltage rating should I choose 6.4 kv indicator or what? And does it work for ungrounded system? In the first case when the neutral point isn't grounded voltage indicator will indicate avoltage or not?