Hello. I am looking for some help witht the description of Power Transformer cooling type designations.
I am looking at two transformers with similiar characteristics.
The first is a 115 KVA 3 phase transformer with the following MVA and cooling designations:
15/20/25 MVA (oil filled with cooling radiators/fins)
ONAN/ONAF/ONAF
Now I believe that these designations are as follows:
ONAN - oil natural, air natural; indicating that both the air and oil are allowed to flow and release heat through natural convection.
ONAF - oil natural, air forced (with fans running); forced air flow over the cooling fins and radiators.
The second transformer has the following rating 115 kVAC, 3 ph:
ONS/ONP/ONPP
ONS -?
ONP -?
ONPP -?
I think that these are similar designation but I am not completely sure (or even the French designation?). Could somone either explan these designations or point me to a good information source?
Thanks,
On your first transformer, Did you mean the last of the options being OFAF (Forced oil and forced air)i.e. both oil and air are moved by force. Oil is pump circulated.
I don't know about the markings on your second transformer, but they should mean the same I guess.
IEEE Std C57.12.00-2000 Liquid-Immersed Distribution, Power and Regulating Transformers §5.1 ‘Cooling classes of transformers’ [noted as consistent with IEC 60076-2: 1993] does not list a “P” desgnation .
fwiw, Google search for "ONS/ONP" gives a bunch of transformer hits. Still don't know what it means.
Eng-tips forums: The best place on the web for engineering discussions.