mauner said:
Is there a significant diffence in the specific gravity of ODWF and OFAF/OFAN?
Not quite sure where that was going:
ODWF = Oil Directed, Water Forced
OFAF = Oil Forced, Air Forced
OFAN = Oil Forced, Air Natural
Questions:
Why are you changing the OD** designation to OF**? There seems little point in interfering with the internal oil flow for the transformer. The oil directors are usually intended to provided additional cooling at likely hotspots within the design. Are you implying that you are going to remove them?
Using OFAN is a relatively unusual mode - ONAF is the more common intermediate step prior to OFAF as it accumulates wear on the easy-to-maintain external fans and minimises running hours on the pump. Fan maintenance on an ONAF design typically doesn't require the transformer to be out of service unlike pump maintenance on an OFAN design (unless you have redundant pumps and isolation valves for each pump - a rare luxury except on very large or system-critical transformers!)
You will almost certainly have a lower pressure drop across a finned air radiator bank than an oil/water heat exchanger. You should check that the pump is suitable for service at a lower pressure, higher flow situation. Changing the pump performance may have knock-on effects on the efficacy of the oil directors at cooling the hot areas of the transformer. You should study the oil flow path very carefully and try to ensure that the conditions do not change significantly from the original design.
The best people to discuss this with are the transformer's manufacturer. What have they said about this proposal?
----------------------------------