If I have a 3 phase transformer rated at 30kVA, 600V primary, 120/208V secondary:
Ip=[30x1000]/[600x1.73]=28.9A (then multiply by 1.25 for code) and the cable size would be #8AWG
Is=[30x1000]/[208x1.73]=83.3A (then multiply by 1.25 for code) and the cable size would be #2AWG
And for a 1 phase transformer rated at 30kVA, 600V primary, 120/240V secondary:
Ip=[30x1000]/[600]=50A (then multiply by 1.25 for code) and the cable size would be #6AWG
Is=[30x1000]/[240]=125A (then multiply by 1.25 for code) and the cable size would be #1/0AWG
I'm going by Table 2 in the CEC for cable size and 90 deg. rated. Is this correct? I'm out of my element on this one. Just wondering if there is other factors I missed. The breaker on the primary would be set to trip to protect the cable (125% primary rated current).
Thanks,
thenoob